A couple of weeks ago we had a lightning strike somewhere close to the house. We know this because we lost both garage door openers, the sprinkler controls, and the ATT Uverse modem. Well come to find out it also popped a couple of breakers.
These are "ARC Fault" breakers. I replaced them with new ones. So I thought I fixed the problem, but noooooo. I have one that will not behave.
It seems when I turn on the treadmill, it pops the breaker (one of the arc fault units). The same happens with the paper shreader and the TV on (same breaker circuit). It does not pop with a iron however. So I seems to be related to the motor driven things, since I think the iron draws more amps than the shreader.
Any suggestions???? I did already try switching the offending one with a different one.
Have you tried those that are tripping on other circuits? I would probably replace all the electrical outlets on that circuit and see if that helps. If that does not work, you will probably have to do some wire pulling on that circuit.
if that is a grounding outlet (i cant see it) it may be the arc of the lightning may have jumped the breaker. and jumped between, melted, and arced wires together somewhere in that circuit---breaker aint at fault, and the iron may have just come short of tripping it
__________________
94 f250 idi turbo sc e4od alum fac rims 149,289 --dana 60 frt with posi--10.25 rear w/posi--shouldnt get stuck!! ats turbo 3" parts on--what a diff from stock turbo!!!!!--- also 96 F250 with 305,000 is fixed!!-- 7.3 rattler-also 85 6.9-needs new engine!! tired!!
I'm not an electrician but I would imagine you would want to shut off the breaker and test for continuity/resistance between the hot and ground at the outlets and try to isolate the issue.
I'm not an electrician but I would imagine you would want to shut off the breaker and test for continuity/resistance between the hot and ground at the outlets and try to isolate the issue.
Yup. A simple DVOM will do this.
Start at the panel by isolating the three wires in the circuit by disconnecting them.
Then probe the ends while checking resistance between all three wires. If you have continuity then it's not the breaker (make sure there are no GFCI's on the circuit, if so isolate them) Do this on the entire circuit at each outlet until you isolate the faulted portion of wire and start cutting drywall.
A typical DVOM tests for resistance and continuity at 9 Volts or less. For locating compromised insulation, you need a hipot ("high potential") tester which will put a few thousand volts on the circuit and measure leakage, arcing or flashover current.
It's also possible that one of your new breakers is overly sensitive. Have you tried swapping breakers within the panel?
__________________
-
Douglas Campbell, P.E.
1986 Isuzu P'up, 177,673.8 miles.
- Hella headlights (highly recommended)
- DOT C-2 back end (also recommended)
- R-12 air conditioner converted to R-406a. Saved ozone and money
- 4.1:1 final drive converted to 3.4:1. Quieter, better mileage but it's a good thing I live in the flat Midwest.
- 9/22/2007, age 21: Still running well when reluctantly sent away for reincarnation, due to body & frame rust.
The AutoGuide.com network consists of the largest network of enthusiast-owned enthusiast-operated automotive communities.
AutoGuide.com provides the latest car reviews, auto show coverage, new car prices, and automotive news. The AutoGuide network operates more than 100 automotive forums where our users consult peers for shopping information and advice, and share opinions as a community.