two wires on one circuit breaker

On a regular 120v house circuit breaker (I use Square D breakers) where the hot wire attaches to the breaker (see photo) there are two indentations for wires. Are you allowed to hook up two wires to two separate circuits on one breaker? I just want to know if this is allowed per the NEC.
__________________
Shimon Mor
1985 F250XL, 6.9L, C6, 4x4 (BW1345), Dana 44HD front, Dana 70 LS 3.54 rear, 190,000 miles, Rebuilt longblock (88,000 miles), ARP studs, electric fuel pump, Edelbrock Performer IAS shocks, Velvet-Ride Shackles, Firestone Airbags all around, Transfer Flow fillnecks, lots of gauges, Line-X, Jordon Brake Controller, B&M Stacked Plate Transmission Cooler, TCI Aluminum Transmission Pan, Banks Sidewinder (wastegated)
shimonmor is offline   Reply With Quote Quick reply to this message
Sponsored Links
Advertisement
 
Old 09-09-2007, 11:00 AM   #2 (permalink)
Senior Member
 
Join Date: Nov 1999
Location: Central WI.
Posts: 493
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

"Are you allowed to hook up two wires to two separate circuits on one breaker?"

YES.
__________________
While doing other things I often wish I were hunting
While hunting I seldom wish I were doing anything else
Wapitibill is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 11:24 AM   #3 (permalink)
Senior Member
 
FINE69's Avatar
 
Join Date: Jun 2005
Location: Pittsburgh, PA
Posts: 1,295
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

Yes you are allowed. No, its not a good practice.
__________________
2009 F350 CCLB Larry-at, 6.4, all the toys....

http://community.webshots.com/user/FineFord
FINE69 is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 12:09 PM   #4 (permalink)
Lifetime Supporting Member
Lifetime Supporting Member
 
Join Date: Apr 1999
Location: Westchester, New York
Posts: 602
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

as long as the total circuit does not exceed the NEC requirements. Will it work YES is it smart NO

Excerpt from the Fester academy of electricity::

If it doesnt spark,blow up or melt, it is no good........
__________________
2008 F-450 Lariat loaded on order 7/3/07 delivered 9/13/2007 Pueblo Gold and all the goodies except Nav radio and moonroof and Fisher 8'6" X-blade

2005
F-350 Lariat LOADED CC SRW LB 6.0 SOLD
Med. Wedgewood Blue
All Options except moon roof
8'6" Fisher X-blade SS
2003 PSD 6.0 Lariat CC SB SOLD
All options but the moon roof
Scottb NY is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 12:12 PM   #5 (permalink)
Senior Member
 
Join Date: Sep 2000
Location: CalEfornia
Posts: 3,631
My Photos: (8)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

There is nothing wrong with it but both wires have to be rated to carry the full current of the breaker.
__________________
2000 F250 CC, PSD, Lariat, 4X4, DP Tuner 80HP PCM, AIS air filter, 4" Magnaflow SS Exhaust, Isspro Overhead Gauges, In-tank mod, Homemade CCV, AIH delete
1985 Jeep CJ7
2011 Hyundai Sonata 2.0T
2003 Yamaha Kodiak 450

"Extremism in the defense of liberty is no vice. And moderation in the pursuit of justice is no virtue." - Barry Goldwater

"They that can give up essential liberty to obtain a little temporary safety
deserve neither liberty nor safety." Benjamin Franklin

"What you want is irrelevant, what you have choosen is at hand." - Mr. Spock
RenoF250 is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 12:13 PM   #6 (permalink)
Senior Member
 
Join Date: Apr 2000
Location: Sedro-Woolley, WA
Posts: 1,338
My Photos: (17)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

<div class="ubbcode-block"><div class="ubbcode-header">Originally Posted By: Fine69</div><div class="ubbcode-body">No, its not a good practice. </div></div>

Could you elaborate? I am curious.

I have a 15A breaker in the garage that feeds only an outside motion-detecting light (2 100W bulbs). I would like to add another similar light on the backside of the garage. The CB sub-panel in the garage is midway between the two lights. So I figured the easiest way to hook up the new light is on the same breaker rather than running wiring between the two lights or adding a junction box between the two runs. I could add another breaker but the sub-panel isn't that large and I don't want to go to those two-in-one-slot breakers.
__________________
Shimon Mor
1985 F250XL, 6.9L, C6, 4x4 (BW1345), Dana 44HD front, Dana 70 LS 3.54 rear, 190,000 miles, Rebuilt longblock (88,000 miles), ARP studs, electric fuel pump, Edelbrock Performer IAS shocks, Velvet-Ride Shackles, Firestone Airbags all around, Transfer Flow fillnecks, lots of gauges, Line-X, Jordon Brake Controller, B&M Stacked Plate Transmission Cooler, TCI Aluminum Transmission Pan, Banks Sidewinder (wastegated)
shimonmor is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 12:14 PM   #7 (permalink)
Lifetime Supporting Member
Lifetime Supporting Member
 
Join Date: Apr 1999
Location: Westchester, New York
Posts: 602
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

that would be fine as long as you do not start adding more and more to it
__________________
2008 F-450 Lariat loaded on order 7/3/07 delivered 9/13/2007 Pueblo Gold and all the goodies except Nav radio and moonroof and Fisher 8'6" X-blade

2005
F-350 Lariat LOADED CC SRW LB 6.0 SOLD
Med. Wedgewood Blue
All Options except moon roof
8'6" Fisher X-blade SS
2003 PSD 6.0 Lariat CC SB SOLD
All options but the moon roof
Scottb NY is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 02:54 PM   #8 (permalink)
Senior Member
 
Join Date: Aug 2000
Location: Spring Valley, AZ.-Clatskanie,OR
Posts: 1,081
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

...and as long as you ascertain the only existing circuit/load is the 2-100 watt lamps. There are many 'sneak circuits' that will suprise you when you find them.
BTW: the 'piggyback' or 'halfdeck' or 'duplex' breakers are very suitable for single slot replacement.
bilbo is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 03:32 PM   #9 (permalink)
Senior Member
 
FINE69's Avatar
 
Join Date: Jun 2005
Location: Pittsburgh, PA
Posts: 1,295
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

<div class="ubbcode-block"><div class="ubbcode-header">Originally Posted By: shimonmor</div><div class="ubbcode-body"><div class="ubbcode-block"><div class="ubbcode-header">Originally Posted By: Fine69</div><div class="ubbcode-body">No, its not a good practice. </div></div>

Could you elaborate? I am curious.

I have a 15A breaker in the garage that feeds only an outside motion-detecting light (2 100W bulbs). I would like to add another similar light on the backside of the garage. The CB sub-panel in the garage is midway between the two lights. So I figured the easiest way to hook up the new light is on the same breaker rather than running wiring between the two lights or adding a junction box between the two runs. I could add another breaker but the sub-panel isn't that large and I don't want to go to those two-in-one-slot breakers. </div></div>

The reason I say its a bad practice is I've seen too many breaker screws loosen due to high current flow. I've had inspectors make me change existing installations that my guys didn't install. The inspector said, while yes, it is legal by code, he would rather see a splice in the panel where you take the 2 wires off the breaker, splice them onto one wire, then land that wire on the breaker. Basically, he just said it was a bad habit to get into. Before anybody says you shouldn't splice in panels, yes, I think that is a bad practice also, but again, perfectly legal as long as all the conductors being spliced have the same rated ampacity. So to answer your wiring question. If I were you, I would just run a new wire to the new location, using the same size wire as the old light, and make a splice in the panel. Again, be sure to use all the same size wire, which for a 15 amp circuit is #14 copper.
__________________
2009 F350 CCLB Larry-at, 6.4, all the toys....

http://community.webshots.com/user/FineFord
FINE69 is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 06:57 PM   #10 (permalink)
Senior Member
 
Seafarer12's Avatar
 
Join Date: Jan 2005
Location: Austin, TX
Posts: 2,581
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

You can run two conductors to one lug but that is max. I try to keep it to one unless I cant help it.
__________________
Massey 65
Seafarer12 is offline   Reply With Quote Quick reply to this message
Old 09-09-2007, 08:59 PM   #11 (permalink)
Senior Member
 
Swellmel's Avatar
 
Join Date: Apr 2006
Location: St Charles,Missouri
Posts: 350
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

<div class="ubbcode-block"><div class="ubbcode-header">Originally Posted By: shimonmor</div><div class="ubbcode-body">On a regular 120v house circuit breaker (I use Square D breakers) where the hot wire attaches to the breaker (see photo) there are two indentations for wires. Are you allowed to hook up two wires to two separate circuits on one breaker? I just want to know if this is allowed per the NEC. </div></div>

Isn't that called "Double Lugging" and is a big NO-NO?
__________________
2002 F350 Red PSD Auto SC/LB SRW 4x4 Tymar Intake 4"Dual Exhaust DI 6 position twisty knob BTS 4R100 Vegistroke V3
Swellmel is offline   Reply With Quote Quick reply to this message
Old 09-10-2007, 08:07 PM   #12 (permalink)
Senior Member
 
Join Date: May 2000
Location: bayville new jersey
Posts: 1,318
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

i ve been told in the past that a service panel is not to be used as splice/conjunction box.... only in case s of service upgrade requiring wires to be lenghtened to reach circuit breakers.

i d have to agree, double lugging is not a good practice.

all up to the local inspector s i guess.
__________________
'12 mercedes s350 bluetec, yes it s a diesel ! !
'12 gmc sierra slt cc, lb, duramax, carbon blk outside, blk leather inside.
'08 mb sl550, my little red its not a corvette
'77 450SL benz , sold 6/13, but still in jersey ! !
'91 350sdl turbo diesel benz
'10 MAZDA 6i, DAUGHTERS RIDE
'90 560sel benz.
hapaschold is offline   Reply With Quote Quick reply to this message
Old 09-10-2007, 10:09 PM   #13 (permalink)
Senior Member
 
Join Date: Apr 2000
Location: Sedro-Woolley, WA
Posts: 1,338
My Photos: (17)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

<div class="ubbcode-block"><div class="ubbcode-header">Originally Posted By: hapaschold</div><div class="ubbcode-body">all up to the local inspector i guess. </div></div>

Yes, it's up to the inspectors. I had a new 200A main breaker panel installed when I moved in and the electrician had to extend a lot of the wires in the panel because the old panel was a lot smaller so there are numerous splices in the new panel and the inspectors passed it. I actually don't see why splices or connections in a CB panel would be any different than in a junction box.
__________________
Shimon Mor
1985 F250XL, 6.9L, C6, 4x4 (BW1345), Dana 44HD front, Dana 70 LS 3.54 rear, 190,000 miles, Rebuilt longblock (88,000 miles), ARP studs, electric fuel pump, Edelbrock Performer IAS shocks, Velvet-Ride Shackles, Firestone Airbags all around, Transfer Flow fillnecks, lots of gauges, Line-X, Jordon Brake Controller, B&M Stacked Plate Transmission Cooler, TCI Aluminum Transmission Pan, Banks Sidewinder (wastegated)
shimonmor is offline   Reply With Quote Quick reply to this message
Old 09-10-2007, 11:12 PM   #14 (permalink)
Senior Member
 
Join Date: Aug 1999
Location: Penn Valley, Ca
Posts: 6,940
My Photos: (9)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

Lots of pontificating on here but I am certain the code addresses this subject specifically, I just cannot find it. For neatness purposes I would rather have two wires under one lug so long as it was made for that, than to have a wire nut in the panel if it was not necessary. From practical experience it will work fine so long as the wires are equal size. Do not even think about it if one is a 14 and one is a 12. The square "washer" will cock on the screw and might not give correct clamping pressure to the smaller wire; if they are the same size it will be more or less level and not have this problem.

Birken
Birken Vogt is offline   Reply With Quote Quick reply to this message
Old 09-11-2007, 11:01 PM   #15 (permalink)
Senior Member
 
Join Date: Mar 2001
Location: Michigan
Posts: 253
My Photos: (0)
Feedback Score: 0 reviews
Re: two wires on one circuit breaker

You can also replace the single breaker with a "piggy back" which gives you two breakers in one space. These are used to increase your breakers with out having to buy another panel.
Your idea will work, but if one lite should short out, it could take out anything down stream of it (2nd lite). With the "piggy back" only one side (lite) would trip. Not all inspectors will approve of your idea or mine. Technology moves faster than code books.
__________________
1994 F250 HD, IDI Diesel, 3:55 gears, K&N filter, Hayden Tranny Cooler, Monroe HD SensaTrac shocks, dual pillar pod with temp & tranny guage, poly fuel tanks
caseyj is offline   Reply With Quote Quick reply to this message
Sponsored Links
Advertisement
 
Reply

  Diesel Forum - TheDieselStop.com > Other Topics > Other Technical Questions

Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the Diesel Forum - TheDieselStop.com forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.
User Name:
If you do not want to register, fill this field only and the name will be used as user name for your post.
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



Wheel & Tire Center

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 02:41 AM.



Powered by vBulletin® Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.6.0

vBulletin Optimisation provided by vB Optimise (Pro) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.